New construction, single family home, home owner wants wifi smokes. 120vac non interconnecting through the wiring.
I say nay, what say you?
I say nay, what say you?
As I said, this is new work, a new home.What says local codes? The NEC is not the only factor in play.
Most allowances for non-wired interconnect are for retrofit in old work.
The home owner is out of luck. See here for NH requirements. He can probably also put in the wifi devices, but still needs the 120 AC interconnected devices, unless he goes to the state fire marshall for a variance. See 907.2.11.3 in the building code regarding interconnection.
If they are AC powered and wifi interconnected I think they pass the requierments.