dereckbc said:Anyone know what the input impedance to a WIGGY is? Looked on the web and cannot find it. Or put another way how much current it draws when connected to 120 VAC.
racerdave3 said:Good question that I don't have the answer to, although I wouldn't suspect it to be all that much. You could plug the Wiggy in to test a receptacle then put a clamp on amp meter on one of the leads and see what it reads.
dereckbc said:Or put another way how much current it draws when connected to 120 VAC.
Of course, it does; it's an inductor.iwire said:I will try to test mine when I get a chance, at 480 it draws a pretty good spark.
LarryFine said:Of course, it does; it's an inductor.
iwire said:To be honest Larry I do not know what that really means.
All I know is it is a coil and has a large inrush current.
Is that what an inductor is?
iwire said:I don't have 480 here at the house unless I backfeed a control transfomer.....
tallgirl said:When do you expect to have those test results for us? :grin:
What would be interesting is to put a storage scope across one of the test leads and whatever you're testing and measure the voltage spike when you remove that lead.
iwire said:Not sure where the control trans is located, it could be out in the unheated garage.....meanaing I ain't going out.
I have a BK Precision 2120 scope, to be honest I really don't know how to use it, I also have (or maybe had) a storage unit that went with it. I think the storage unit went out during a clean up of the basement.
![]()
A lot of old time electricians like me found out about that when using a flashlight continunity tester to test transformer windings...if you were touching the transformer leads when you disconnected the tester, you got bit.What happens with an inductor at the time the circuit is opened is the magnetic field in the inductor begins to collapse. This induces a current in the inductor, and that current has some voltage (I think this is Faraday's Law -- one of the EE's here can check me). If the induced voltage is high enough, arcing can occur. This, conveniently, is the basic principle behind the "breaker-point ignition" from when we were all kids.
don_resqcapt19 said:Julie,
A lot of old time electricians like me found out about that when using a flashlight continunity tester to test transformer windings...if you were touching the transformer leads when you disconnected the tester, you got bit.
Don
iwire said:To read the 120 circuit the solenoid tester used 25.42 ma.
Jumping from 120 to 240 volts resulted in the following
The Solenoid tester required 52.8 maBob, thanks that answers the question, the input impedance is roughly 4.6K-ohm.
It also tells me I can make a resistive equivilant by using a 4.7 K-ohm resistor. Only problem is to make it work up to 480-VAC would require a 50-watt resistor, otherwise 5-watt @ 120. Think I will stick with my ole trusty 50K-ohm home-brew.
tallgirl said:I am surprised that wiggys don't have something built in to suppress the arc.
That would dampen the movement and prevent it from vibrating a key feature electricians look for.tallgirl said:I am surprised that wiggys don't have something built in to suppress the arc. If I ever get around to replacing it I'll open it up and see what the heck is actually inside one and if there is some way to suppress the arc with a big, fat capacitor and a resistor.