We should be able to agree that when the POCO taps a MV three phase line with single phase, the tap neutral is half of the two wire circuit and that voltage drop on the neutral is the cause of neutral to earth voltage (NEV).
Is it plausible that if the utility reduces the grounding resistance at each point along the line where the neutral is bonded to the earth by driven rods, that the voltage drop will be reduced and consequently the NEV will be reduced? If the voltage drop on the neutral is reduced, does this translate to smaller losses and less money spent on delivering the product?
I am promoting ground resistance testing for new POCO construction and if it can get tied to money, I can probably sell it.
Is it plausible that if the utility reduces the grounding resistance at each point along the line where the neutral is bonded to the earth by driven rods, that the voltage drop will be reduced and consequently the NEV will be reduced? If the voltage drop on the neutral is reduced, does this translate to smaller losses and less money spent on delivering the product?
I am promoting ground resistance testing for new POCO construction and if it can get tied to money, I can probably sell it.