aks20000
Member
- Location
- San Francisco
- Occupation
- engineer
I have 200 amp service to my home, which is split between two sub panels - each rated at 100 amp.
One panel caters to house circuits and has almost used up its capacity per the load calculation guidelines of electrical code for my city.
The other panel serves two ACs and a Tesla charger. This panel is also not having any extra capacity , even though only three circuit breakers are there with space for 17 more .
The ACs are very old but functional and account for 35 amp load each. These load calculations were done following the code guidelines and approved by my City during Tesla charger installation.
I am planning to add 4 single zone heat pumps , each rated for 15 amp each.
These heat pumps will make two old ACs redundant and I will switch off the CBs for these ACs. But I don't want to dismantle these units and keep it as backup. The old ACs and new heat pumps will never ever run simultaneously.
Will switching off these ACs result in creating scope for adding these heat pumps and be in compliance of electrical code ?
If switching off will not be considered as "removed", is there any alternative way to keep the units available for running if needed and still not count towards new load calculation ?
One panel caters to house circuits and has almost used up its capacity per the load calculation guidelines of electrical code for my city.
The other panel serves two ACs and a Tesla charger. This panel is also not having any extra capacity , even though only three circuit breakers are there with space for 17 more .
The ACs are very old but functional and account for 35 amp load each. These load calculations were done following the code guidelines and approved by my City during Tesla charger installation.
I am planning to add 4 single zone heat pumps , each rated for 15 amp each.
These heat pumps will make two old ACs redundant and I will switch off the CBs for these ACs. But I don't want to dismantle these units and keep it as backup. The old ACs and new heat pumps will never ever run simultaneously.
Will switching off these ACs result in creating scope for adding these heat pumps and be in compliance of electrical code ?
If switching off will not be considered as "removed", is there any alternative way to keep the units available for running if needed and still not count towards new load calculation ?