Have an old old A/C unit, 230/208V, 15.8A/16.5A with no max CB size listed since that was not a requirement when it was manufactured.
It is clear that the CB size must be 30A on my 208V circuit. But what wire size needs to be used? I have an existing circuit that is #12 that I would like to use. If it were a regular motor circuit #12's would be fine.
California Elec Code (1999 NEC) Art 440 Part D (Branch Circuit Conductors) section 440-33, ex 2 says that for conductor sizing Part 'G' applies.
Part G says that the appliance shall be treated as a single motor appliance where all of the following conditions are met: 1 - cord and plug connected , 2 - not over 40A 250V, 3- Total rated load is on nameplate, 4 - Branch circuit CB/Fuse does not exceed ampacity of the wiring.
What if the four conditions are _NOT_ met? I can't go back to 440-33 because it directs me to Part G. I'm going around in circles!
It is clear that the CB size must be 30A on my 208V circuit. But what wire size needs to be used? I have an existing circuit that is #12 that I would like to use. If it were a regular motor circuit #12's would be fine.
California Elec Code (1999 NEC) Art 440 Part D (Branch Circuit Conductors) section 440-33, ex 2 says that for conductor sizing Part 'G' applies.
Part G says that the appliance shall be treated as a single motor appliance where all of the following conditions are met: 1 - cord and plug connected , 2 - not over 40A 250V, 3- Total rated load is on nameplate, 4 - Branch circuit CB/Fuse does not exceed ampacity of the wiring.
What if the four conditions are _NOT_ met? I can't go back to 440-33 because it directs me to Part G. I'm going around in circles!