unless you are using NM cable / or have an ambient tempt. over 122 degrees/ or more than 6 ccc in a raceway.
 

frizbeedog

Senior Member
Location
Oregon
augie47 said:
unless you are using NM cable

Why the restriction fo NM cable?

Considering the ampacity given in the 60 deg. column, 55 amps, and considering no adjustments, why not a 60 amp OCPD for this wire?

250.6(A) does not list 55 amps as a stadard rating of a fuse or circuit breaker.

So I'm thinking 240.4(B) will allow this to be protected at 60 amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
frizbeedog said:
Why the restriction fo NM cable?

Considering the ampacity given in the 60 deg. column, 55 amps, and considering no adjustments, why not a 60 amp OCPD for this wire?

250.6(A) does not list 55 amps as a stadard rating of a fuse or circuit breaker.

So I'm thinking 240.4(B) will allow this to be protected at 60 amps.

I agree unless the load is greater than 55 amps.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I stand corrected.. brain cloud
NM would be ok. with a load not over 55 amps.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You could likely use the #6 THHN on a 70 amp CB if the load is 65 amps or less since 65 amps is not a standard size.
 

C3PO

Senior Member
Location
Tennessee
jimmyglen said:
I was just thinking about this this morning

we run #6 NM for our ranges etc on a 50 amp breaker

shouldnt we be running #8 for 50 amp

what am i missing?

If you are running a #8 NM it would have to be on a 40A breaker.
If you are tunning #8 THHN you could put it on a 50A breaker.
 

stickboy1375

Senior Member
Location
Litchfield, CT
RossQualityElectric said:
this might be kind of off topic but some times i will feed a 50 amp hottub dissconnest with a 60 amp braker useing number 6 wire


Why would you do that? WHy not just buy the right size disconnect to begin with?
 