augie47 said:unless you are using NM cable
frizbeedog said:Why the restriction fo NM cable?
Considering the ampacity given in the 60 deg. column, 55 amps, and considering no adjustments, why not a 60 amp OCPD for this wire?
250.6(A) does not list 55 amps as a stadard rating of a fuse or circuit breaker.
So I'm thinking 240.4(B) will allow this to be protected at 60 amps.
Me Chief Brain Cloud. Keep up the good work, Little Works With Wires.augie47 said:I stand corrected.. brain cloud
Yes! and Yes! :grin:EL CHUAPY said:Can I Feed A Comercial Panel With # 6 Thhn Is The Breaker Is A 60 Amp
jimmyglen said:I was just thinking about this this morning
we run #6 NM for our ranges etc on a 50 amp breaker
shouldnt we be running #8 for 50 amp
what am i missing?
RossQualityElectric said:this might be kind of off topic but some times i will feed a 50 amp hottub dissconnest with a 60 amp braker useing number 6 wire