Wire and Breaker Size for Car/Automotive Lift
United States
Electrical Apprentice
Hey guys.
Installed wiring for a 2 post car lift in a garage and wanted to double check on some things.
- Motor Nameplate Attached -
Motor is single phase, 2hp, 240v, 12-16 amps
I went by the manual of the lift which said to size wire for 20 amps. Also said to use 20 amp fuse.
I ran 12/2 romex from main panel up to attic and then fed down to a junction box above the lift. From there I ran 12/2 armorlite mc cable down to a double-pole 20 amp switch and then to the lift.
Though I've now found pretty much any other forum saying to use 10awg wire w/30amp breaker.
Does the NEC require a higher breaker such as a 30amp for the motor? Was this installation done right?
Thanks
The label is printed incorrectly, which is misleading; the higher current applies to the lower voltage.
Therefor, on 240v, the current is 12a; a 20a circuit is adequate.
Even with 12ga wire, you can increase the breaker size if needed to start the motor.
How would I know if a greater breaker is needed? Would it be if the lift breaker ever trips?