Wire and fuse sizing for elevator iso transformer

Status
Not open for further replies.

Fred Shenkman

Member
Location
Ny,Ny
Hello all,

This is for elevator application where iso transformer directly supplies a KEB pwm a/c drive.

Looking for input and advise on sizing primary side and properly fusing same. Following is example to use. 85kva 460/460 3 phase.

So using kva=V*I*1.732/1000 would give me 106.69A.

Typically would use THHN #2 or #1 depending on run length?

What would be the rule of thumb for picking proper fuse size?

Side note,I realize that this is not really a influence to the questions but the elec insp used this in his violations, Gearless PM motor being used with following data: 174V, 105A, 32HP.

He commented that that if time delay fuse in mainline it should be 106x175% or for non time delay 106x300%. Thats crazy!
 