I'm building a 125HP enclosed VFD panel with a high SCCR (meaning large power distribution), bypass contactors, 400A disconnect, line reactor, brake module, and other miscellaneous devices. On top of all that, I'm required to provide 20% spare space. Because I have to show all this on a layout, I need to squeeze everything together. I'm really looking close at the wire bending space. The 125A motor circuit will be using 3/0 conductors. UL 508A only seems to cover conductors entering or leaving the enclosure. The same appears to be true of 312.6. I can't find anything about the conductors that begin and end inside the enclosure. Can anyone comment on this? Over the decades, I have seen a lot of very tight internal wiring on large power control panels, so maybe that's the reason they can get away with it. Maybe there are no restrictions...?? Also, this section only seems to refer to "wire bending space". It doesn't say anything about the bending radius of a conductor. In other words, you just have to provide the space. You could bend the wire sharper (within reason) if you want. 300.34 does have conductor bending radius requirements, but that's for conductors greater than 1000V. I guess we would have to comply with conductor manufacturers instructions, but I haven't got that far... Thanks in advance.