I hate to bring up this since it has been before, but I wanted to clarify what I already know or have read regarding NM cable inside a buried PVC conduit;
1. 24" depth (under grass)
2. Grey PVC pipe (not white)
3. A yellow (?) marker tape run just above the pipe.
4. UF rated Roimex (UF) or THWN indvidual conductors
5. NM is allowd in conduit ABOVE ground (non wet locations).
6. Less than 60% fill factor in conduit
Ok, how's that??
Questions;
A. What is the "heating" issue within conduit?
B. Are GFI outlets required INSIDE a garage?
C. Expansion joints, are they required on the horitzontal and vertical runs?
D. Can neutrals and 'hots' be 'ganged' within a single screw terminal?