Lady,
The ampacity of 500 kcmil THHN copper conductors, with 600v insulation, in an ambient temperature of 86?F, with not more than 3 current carrying conductors in the raceway, is 430A. Changing any of these conditions of use will change the ampacity.
Most breakers have lugs rated at 75?C which requires that the ampacity be reduced to 380A. This (as I understand it) is required to protect the breaker, not the conductor. Article 240.4(b), by allowing the next larger breaker to be used, implies that breakers are not damaged by the small increase in current that results.
Edit: So if you believe that breakers can be damaged by the additional current, and choose to change the specs on a project accordingly, I respect that. Just don't expect a contractor, once he has won a bid, to oversize the conductors on his own.