Re: wire capacity

the #8 is in BX for an air conditoning disconnect.
upgrading to a 5 ton compressor with a 50 amp draw
 
Re: wire capacity

#8 copper is rated 40A per table 310-16. 1999 NEC 110-14(c)(1)(a) says that the 60 degree C column ampacity must be used unless the terminations at both ends are labeled for a higher temperature. You may also need to consider derating for ambient temperature in selecting the conductor size.
 
Re: wire capacity

The distance of the run is never a factor in determining a cable's ampacity. It may, however, become a factor in providing sufficient voltage at the end of the run. Sometimes, you will need to use a larger wire for the same current, in order to limit voltage drop. But 30 feet is generally not a long enough run to worry about voltage drop.
 
Re: wire capacity

What is the minimum circuit ampacity shown on the equipment nameplate? The conductor ampacity must equal or excced the minimum shown on the namplate. If the minimum circuit ampacity is not shown, you must have conductors sized for at least 125% of the full load running current.
Don
 