Wire Clamps for Routing Grounds

Status
Not open for further replies.

SDEngineer

New User
Location
57064
Occupation
Project Manager
An inspector is requesting that we replace the wire clamps used to route GECs because they could induce current and cause destructive heat to the grounding conductor. The clamps used are G90 with a vinyl plastisol coating 32 mils thick and are fastened to the steel structure of the building. The ground conductors are insulated THHN. I don't believe that the duration would be long enough to induce that heat required to damage the conductor. Does anyone else have experience with this scenario?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Hmmm. Did the AHJ cite a rule?
If it’s not a lot of clamps, they’re one hole plastic cable clamps. I get them at ace hardware in the metal parts drawers
 