wire color code
michael.howard
New member
working a production as a maintenance tech. and heard that dc circiut wires need to be blue but can not find any refernce to that fact just wnated some insight on the subject.
pwhite
Re: wire color code
michael,
try nfpa 79 - electrical standard for industrial machinery. page 79-31 section 61 (wiring methods & practices).
section 16.1.3 "the use of other colors for the purpose of identification shall be as follows:"..... "- Blue: Ungrounded dc control conductors"
hope this helps.
most of the industries i have worked with use blue colored wire to designate 24 volts dc, both +24 volts and 0 volt terminal. one customer uses white to designate the 0 volt wire of the 24 volt circuit.
regards,
p white
tom baker
Bremerton, Washington
Master Electrician
Re: wire color code
If its a grounded DC conductor, the required color code per NPFA 79 and its equal IEC standard is white with a blue stripe.
james wuebker
Iowa
Re: wire color code
Where I work we have plastic molding machines. In the control cabinets the colors are:
blue- +24vdv
purple- 0vdc
red- 120vac
black- 240vac
These are Engel machines. I hope this will help.
Bye now!