Thomas Ruffing
New User
- Westlake, OH
- Engineering
What is the correct wire color coding in the US for a 240/480 Volt, Split Phase, 1 Phase, 3 Wire System according to the NEC Code.
White or gray is neutral. Green or green w/ yellow stripe is ground orange is high leg.What is the correct wire color coding in the US for a 240/480 Volt, Split Phase, 1 Phase, 3 Wire System according to the NEC Code.
Light blue for IS (art 504)White or gray is neutral. Green or green w/ yellow stripe is ground orange is high leg.
No other colors are mandated by code that I know of.....
Orange with identifying stripe, brown with identifyimng stripe, & on 3 phase, yellow with stripe.Light blue for IS (art 504)
someone can help me with this, orange and yellow for operating room isolated ground systems?
Most of these site specific NEC requirements do not prevent the color from being used in other locations, unlike grounding and grounded colors are.Light blue for IS (art 504)
And green only became a restricted use color in the 2005 code. Prior to that you were permitted to use green as an ungrounded conductor. It was not commonly used as such, but I have seen it a number of times over the years. No matter what the color may be, you should always use some other method to verify the function of the conductor.Most of these site specific NEC requirements do not prevent the color from being used in other locations, unlike grounding and grounded colors are.
This is why orange means high/wild leg only if a high leg system exists.
I would use Brown and Orange for phases and Gray for the neutral, like if I am pulling a 1 phase circuit off a 480 system.What is the correct wire color coding in the US for a 240/480 Volt, Split Phase, 1 Phase, 3 Wire System according to the NEC Code.
Which is why the NEC did away with color requirements in the mid 70sAnd green only became a restricted use color in the 2005 code. Prior to that you were permitted to use green as an ungrounded conductor. It was not commonly used as such, but I have seen it a number of times over the years. No matter what the color may be, you should always use some other method to verify the function of the conductor.
Some flexible cords can use light blue as a neutral 400.22 I think.Light blue for IS (art 504)
If that is the only voltage system on the premises the only thing that requires any specific identification is the grounded (neutral) conductor and of course equipment grounding conductor.What is the correct wire color coding in the US for a 240/480 Volt, Split Phase, 1 Phase, 3 Wire System according to the NEC Code.
What do you mean by bare aluminum ground? Is this MC-ap cable? This should apply.Newbie question here...I had plenty of left over 12-3 MC with a bare aluminum ground from another job, so I used the red wire for the ground on a couple circuits in my own garage...is that against the NEC? There's no inspector here in rural WV so that's not an issue and I'm sure it's safe because the bare aluminum is grounded to the metal sheath...but I've searched on the code and I'm having trouble finding a clear answer.
250.119(B) Multiconductor Cable.
One or more insulated conductors in a multiconductor cable, at the time of installation, shall be permitted to be permanently identified as equipment grounding conductors at each end and at every point where the conductors are accessible by one of the following means:
(1) Stripping the insulation from the entire exposed length.
(2) Coloring the exposed insulation green.
(3) Marking the exposed insulation with green tape or green adhesive labels. Identification shall encircle the conductor.
Or might it be AC in realityWhat do you mean by bare aluminum ground? Is this MC-ap cable?
You're right it could be AC cable. I guessed MC-ap because I haven't seen much new AC cable in the past decade.Or might it be AC in reality
You don't need to mark the red wire, in your case the aluminum is shunting the coils of the MC making the sheath the EGC. See 250.118Thanks for the answers, gents! I'll mark the red wire as ground for these circuits.
Here's the specific wire:
Southwire 12 AWG 3 Conductor Solid Metal Clad Armored Cable 600V SLVR 55510401 | Zoro
Order Southwire 12 AWG 3 Conductor Solid Metal Clad Armored Cable 600V SLVR, 55510401 at Zoro.com. Great prices & free shipping on orders over $50 when you sign in or sign up for an account.www.zoro.com
And I'm trying to update my location in my profile, but I can't figure that out...feeling not smart. Where do I do that?
Yes, MC-ap. The #10 aluminum gets cut off at the connector.Here's the specific wire: