megloff11x
Senior Member
The standard practice is that 208Y120 is either all black, or black, red, and blue for the lines. 480/277 is either all black or they use brown, orange, and yellow. Usually because the wire is so fat and the price of spools being what they are you just put colored tape on the ends so you can keep track of which line is which. Ground is either bare copper, green, or green/yellow stripe, and can be black with green tape for fat wire. Neutral is usually white or white tape.
In NFPA79 they recommend that Orange or Yellow be almost exclusively used to indicate line Voltage that is NOT de-energized when the main disconnect is off. This would conflict with standard or optional color coding for 480/277.
Further, red is for lower Voltage AC (like a 24VAC on an EMO loop) and blue is recommended for DC Voltages. These could be confused with lines B&C of a 208Y120 3-phase.
They don't suggest a color for the return wire for DC Voltages, which may or may not bond to the incoming ground.
As long as I provide a color chart...
But after all this my question is, what do you like for your wire color schemes when you set up a machine, and how do you deal with the shared colors issue?
Matt
In NFPA79 they recommend that Orange or Yellow be almost exclusively used to indicate line Voltage that is NOT de-energized when the main disconnect is off. This would conflict with standard or optional color coding for 480/277.
Further, red is for lower Voltage AC (like a 24VAC on an EMO loop) and blue is recommended for DC Voltages. These could be confused with lines B&C of a 208Y120 3-phase.
They don't suggest a color for the return wire for DC Voltages, which may or may not bond to the incoming ground.
As long as I provide a color chart...
But after all this my question is, what do you like for your wire color schemes when you set up a machine, and how do you deal with the shared colors issue?
Matt