Wire Depth Near Roof

Green Machine

Member
Location
Tennessee
Occupation
Electrician
I had a conversation with a roofer I've done some work with: he has now twice had one of his guys nail through wire that is too close to his roof deck. He asked how far from his roof deck or wood had to stay. He wanted to know if he really was responsible for knowing where wires are under a roof deck.

I at first assumed 1¼", since that is the distance in walls, but he pointed out that his nails could go as far as 2" to 2½".

Is there a separate code for roof decks from walls?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Why is he using such long nails? They sell them shorter..
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I had a conversation with a roofer I've done some work with: he has now twice had one of his guys nail through wire that is too close to his roof deck. He asked how far from his roof deck or wood had to stay. He wanted to know if he really was responsible for knowing where wires are under a roof deck.

I at first assumed 1¼", since that is the distance in walls, but he pointed out that his nails could go as far as 2" to 2½".

Is there a separate code for roof decks from walls?
I can't recall ever running my NM up near the roof deck. Why are you running it that high?

Also, someone needs to mark, or chalk, some lines to know where to nail. They should only be hitting the trusses or rafters, not shooting nails into the decking where there isn't anything to nail to.
 
Last edited:

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I’ve seen boxes with keyless fixtures attached to roof rafters in attics.
I did a job on lights at a church, in vaulted ceiling. Had some kind of oversized octagon boxes in ceiling. Must have been just below roof panel because 1 had a nail shot into it. I had no practical way to remove it, so I put a wire nut on it.
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I can't recall ever running my NM up near the roof deck. Why are you running it that high?

Also, someone needs to mark, or chalk, some lines to know where to nail. They should only be hitting the trusses or rafters, not shooting nails into the decking where there isn't anything to nail to.
I've seen countless attics with roofing nails missing rafters by an inch or so, or skimming the side.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
I can't recall ever running my NM up near the roof deck. Why are you running it that high?

Also, someone needs to mark, or chalk, some lines to know where to nail. They should only be hitting the trusses or rafters, not shooting nails into the decking where there isn't anything to nail to.
Once the plywood decking is in place they are just shooting roof nails as the shingles are needed into the ply not to the rafters. seen many porcupine roofs (two layers of roofing) and trying to negotiate a low attic and not pierce the top of my head.

Some roofers are screwing down the decking with 2.5 or 3 in deck screws not nails so even if you drilled trough the rafter to a minimum allowed depth it is likely to get hit. But also seen where guys have gone in, usually handymen, and sliding NM over the rafter between the purling and the roof deck, no holes to drill and no staples to pound in, to put in some attic lighting, that's easy to hit.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I can't recall ever running my NM up near the roof deck. Why are you running it that high?

Also, someone needs to mark, or chalk, some lines to know where to nail. They should only be hitting the trusses or rafters, not shooting nails into the decking where there isn't anything to nail to.
The shingles are attached to the decking...very few of the nails will line up with a truss or rafter.
 