stew
Senior Member
- Location
- federal way,washington
I have to install an additional circuit 208 v 3 phase to a new rooftop ac unit. The min circuit amps are 26.5 so I will use a #10 thhn to feed. The max breaker size is 50 so I will use that for a breaker. Hers the rub. I want to put this circuit in an existing conduit with other loads to hit the roof. There are 4 # 10 And 6 # 12 in the pipe now for a total of 10 current carring conductors. How then do I apply the derating of this to correspond to the breaker when the breaker is already larger than the required size for a normal load?