george t. everett
- New York
When adjusting conductor ampacity is the neutral of a 3-wire or 4-wire circuit counted as a current carrying conductor?
Who defines what is a "major portion"? 50.5%? Is there anything specific in the NEC?Originally posted by wirebender:
On a 4-wire,3-phase wye circuit, it is not counted unless the major portion of the load is nonlinear loads(ballasts,etc.).310.15(B)(4)(c). [/QB]
I think the handbook says 50% or more. The odd thing is there is no real definition for non-linear. That also comes in varying degrees... 5% THD, 10% THD, ect. So who decides if the lighting ballasts with less than 10% thd is non-linear?Who defines what is a "major portion"?
Very true. Consider the extreme case. If you load a 3-phase panelboard with all the loads on phases A and B, then C will have no current, and the neutral will carry the same current as A and B. You will see three conductors carrying current.Originally posted by steve66:As far as out phase-phase balance goes: any increase in neutral current is offset by a corresponding decrease in the current in a phase conductor.