Is it acceptable to install 12-2 Romex in a PVC conduit in a slab for a kitchen island? Or do I have to install UF wire in the PVC conduit?
It's on-grade.There is a layer of base under the slab.
Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
The interior of a conduit is not a location; the conductors are located wherever the conduit is located.- As the slab is not above grade, even if the slab is a wet location, 300.9 does not tell us that the interior of a conduit in it is a wet location.
- 300.5(B) tells us that if the conduit is underground, then the interior of the conduit is a wet location.
It is a more specific location compared to the location of the conduit.The interior of a conduit is not a location; the conductors are located wherever the conduit is located.
That is an approximate rule of thumb; the actual rules are in 300.5(B) and 300.9. (Any others I missed?)The interior of a conduit is not a location; the conductors are located wherever the conduit is located.
Indeed, which immediately raises the question of whether a slab cast again compacted base rock, rather than native soil, is "in direct contact with earth."A raceway in a concrete slab in contact with the earth is a wet location by Article 100 definition.