wire nut inside breaker panel

Status
Not open for further replies.

nevsquare

Member
Hi forum members: as a helper I sometimes see a wire nut connection inside a breaker panel where some one came up short. The other day I worked with an electrician that did it and he said it was ok because a connection needs to be inside a box and the breaker panel qualified as such. I came here for a 2nd opinion and thanks for all the info posted here. I usually don't get a full week in since I started in the trade a few months ago and I try to read on this site whenever I have time, Thanks - Gordon
 

iwire

Moderator
Staff member
Location
Massachusetts
nevsquare said:
Hi forum members: as a helper I sometimes see a wire nut connection inside a breaker panel where some one came up short.

Welcome to the forum and the trade. :)


The other day I worked with an electrician that did it and he said it was ok because a connection needs to be inside a box and the breaker panel qualified as such.

First you need to think like the NEC, it would be imposable to put a splice in a panelboard.

Per the NEC definitions this is a panelboard as covered by Article 408, it is missing only the dead front.

PanelGuts.jpg


This one may be much larger then what your used to but to the NEC a panel board is only the 'guts'.

Panelboards are generally mounted in a cabinet as covered by Article 312 and

This is a cabinet as covered by Article 312

10406_300.jpg



When you do commercial work you often have to order the parts separately, when you do residential work you normally use a "Load center" which is a manufacturers term for a cabinet, panel board and cover all shipped together.

The reason I am telling you all this is because in order to find the answer in the NEC you need to know where to look.

The electrician you where working with was correct he can make a splice in a cabinet that contains overcurrent devices.

The rules for doing so can be found in 312.8
 

TOOL_5150

Senior Member
Location
bay area, ca
312.8 Splices and taps can not fill more than 75% of the wiring space in a switch or circuit breaker enclosure.

So, to answer your question - They are allowed.