Randy,
Rodger are we playing with the man... and his choice of words... " ground" and not EGC,
that allowed you to say yes to running 240 through the speicified wire????
there is no trickery to my answer. The ground conductor and EGC are one and the same in this cable assembly, and have nothing to do with my answer.
Allow me to ask more succinctly,
Can you run 240v through 12/2 NM??
The answer is YES. 12/2 with ground has two insulated conductors which can be used as current carrying conductors. A white conductor in this assembly can be reidentified. The bare can not be used as a neutral in this assembly.
Technicaly, 2-12 awg and a ground is an incorrect terminology, correct???
No, this is actually correct terminology, although "with ground" is more common
Randy you are looking to be tricked here, which is not the case.
Look in most any panel or loadcenter in a cable job, (NM, MC, AC etc...) and you will see the white of one or more cables connected to a breaker.
As Bennie points out, a "neutral" doesn't exist in a two wire circuit, it is a grounded conductor and will carry the same current as the ungrounded (attached to breaker) conductor.
Roger