Wire phasing

Status
Not open for further replies.

michael brady

Member
Location
Idaho
Occupation
electrician
I know that you cannot use phase tape on grounded conductors that are #6 or smaller and that you can use phase tape on ungrounded conductors of any size. My question is......can you use phase tape on a green wire so that it can be used as an ungrounded conductor?
 

michael brady

Member
Location
Idaho
Occupation
electrician
Nope. If it's green it's only allowed as an equipment ground. 250.119
250.119 is about terminals. I was asking about using phase tape on a green wire. I can't find the code section that addresses that. Please advise if you know the code section. Thanks for the reply.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
250.119 is about terminals.
Where are you reading that? Here is 250.119, notice the heading.

250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment
grounding conductors shall be permitted to be bare,
covered, or insulated. Individually covered or insulated
equipment grounding conductors shall have a continuous
outer finish that is either green or green with one or more
yellow stripes except as permitted in this section. Conductors
with insulation or individual covering that is green,
green with one or more yellow stripes, or otherwise identified
as permitted by this section shall not be used for ungrounded
or grounded circuit conductors.
Exception: Power-limited Class 2 or Class 3 cables, power
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I should add to be sure you read 250.119 (A) and (B)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Thanks for the info. I have an older code book and obviously the subject matter of 250,119 has changed over the years. I need to get an updated code book. Thanks again.
I guess, your code book must be before 1999.
 