the senario is,
i have a transformer, 30kva, 480 pri, 240 sec,
72 amps max secondary,
im feeding 2 machines 20 amps each
the question is, if each of these machines are
internarlly fused and protected, via disconnects and fuses,
do i need to run wire that sized for the 72amps or can i use the smaller gauge wire provided from the equipment manufacturer?
if using the smaller provided wire, would i then need to provide 20amp, protection at the secondary side??
what or where does the code address this??
we are discussing this one in the shop.