wire protectors, nail plates

Status
Not open for further replies.

Buck Parrish

Senior Member
Location
NC & IN
I have a customer that ran wiring in a log home. He ran the wires surface mounted in between the logs. Then the mud will be put on top of them.

Then he calls me:-?.
Would a long piece of metal 2'' wide an 4' long suffice as a nail protector? It would also keep the mud from direct contact with the wires.
The boxes are made up so conduit would be a pain.
 
It seems the question is really, "What type of wiring was used?" EMT, MC, Romex? I dont think there is a problem with the type of studgaurd you use as much as there could be a problem with the wiring system. Romex or MC would probably not be acceptacle. I would say if the wire is emt, it may be ok .
 
It seems the question is really, "What type of wiring was used?" EMT, MC, Romex? I dont think there is a problem with the type of studgaurd you use as much as there could be a problem with the wiring system. Romex or MC would probably not be acceptacle. I would say if the wire is emt, it may be ok .



It's #12 indoor wire nm (romex)
 
Thats not what i said. What is said was you cant shove a bunch of wet concrete around a romex wire or an mc wire for that matter.
 
If the metallic steel material is 1/16" thick or greater than listing isn't an issue.
 
Why would it require a nail guard at all? It's a log home, you're not hanging drywall or putting up any shear panels. I wouldn't even worry about it. If I had all the wood to attach something to, I'm going to try to go out of my way to not hit the chinking.
 
If the cable is not subject to physical damage for whatever reason log houses might afford, (I never saw the inside of one so I have no idea of the space where the logs meet.) then covering with hat track should be a good way to provide a barrier between the romex and the plaster goop they are slapping on top. If there is a physical damage chance due to 1-1/4" issues, then hat track is not heavy duty enough.
 