Yes usually run without conduit correct? Obviously If a cable type..lllUSE-2 is a cable type in T310.4(A). Seems like an odd specification.
Yes it can be direct buried without conduit. Not sure what colors are available. Southwire does not list BOY colors.Yes usually run without conduit correct? Obviously If a cable type..lll
This would get an RFI as I don't understand installing a cable directly buried in concrete. I read feeders concealed in concrete as the feeders being physically encased in concrete.Yes usually run without conduit correct? Obviously If a cable type..lll
Don was commenting on the poorly written spec that you've posted. It sounds like they want a direct burial cable installed even within the pour without a raceway. Does something else in the spec tell you to use a raceway?Yes understand but normally you would NOT run USE in a conduit, correct?
Actually for service entrance it does say USE-2 is single conductor. So that's wire type, no?
USE-2 can be single or a multi conductor cable assembly.Yes understand but normally you would NOT run USE in a conduit, correct?
Actually for service entrance it does say USE-2 is single conductor. So that's wire type, no?