Yes understand but normally you would NOT run USE in a conduit, correct?

Actually for service entrance it does say USE-2 is single conductor. So that's wire type, no?
 
Yes understand but normally you would NOT run USE in a conduit, correct?

Actually for service entrance it does say USE-2 is single conductor. So that's wire type, no?
Don was commenting on the poorly written spec that you've posted. It sounds like they want a direct burial cable installed even within the pour without a raceway. Does something else in the spec tell you to use a raceway?
 
Also note that unless it has a second rating such as RHW or RHH, USE-2 cannot be used inside a building. In my area most of the USE available is not dual rated.
 