Hi all,
it's been a long time since i posted i had to reregister. i'm now back into the electrical design rather than controls programming.
i cannot remember the code, but i seem to remember that electrical conductors must be rated based on the temperature rating
of the terminal lugs of the circuit breaker box / disconnect.
for example, if the disconnect lugs are rated at 60 degrees c, then you must use the 60 degree column for determining the size of the current conductor.
you would not use the 75 or 90 degree column.
if i am correct, please point me to the code, i have a concern about the wire my coworker says he is going to use.
if i am incorrect, please let me know.
Thanks in advance,
Philip