Does code allow for the reduction of a #8 THWN to #12 as long as it it on a 20 amp breaker?
Does code allow for the reduction of a #8 THWN to #12 as long as it it on a 20 amp breaker?
As is always the case, the devil is in the details.
As has been noted above, using a larger than minimum conductor and changing between minimum and larger conductors in a single circuit is done for many reasons and quite frequently.
You may encounter various limits on doing this.
The big issue that you might encounter is if you are using _cables_ rather than individual wires. #8 NM cable commonly has a #10 EGC (ground) wire. But for 20A circuits, if you increase the size of the circuit conductors you must also increase the size of the EGC by the same amount. So you can't legally use #8 NM on a 20A circuit, even though it would be perfectly kosher on a 40A circuit.
-Jon