I have a client that manufactures a machine using 13 Servo Drives.
All drives start at the same time.
We are selling him the Drives. He is asked for help sizing the wire and Circuit protection devices.
I used 430 part X to size the wire per servo input current.
The Servo is listed as having overload protection for the Servo motor.
I sized the circuit breaker based on Servo input current and table 430.52(C)(1) for a synchronous motor at 250% of the current.
The client is telling me they have never sized the CB's for similar Servo's as large as we recommended.
looking at the system it looks like someone specified a servo system larger than needed, When looking at a total of 13 drives the current really adds up.
They have typically sized the main control breaker for the machine at 30 amps. If I add up all of the rated input currents to size the main control panel breaker I am at closer to 200 amps.
So here are a few questions.
1, was I wrong using 430.52(C)(1) at 250%?
2. Is it acceptable to size the wire as stated above, but size the CB's based on empirical data?
3. The method I used to size the Main Control Breaker was sizing the main panel breaker still a sum of all loads (current) except the largest load, added to the largest breaker. Is this still acceptable or should I look at another method?
Thanks in advance for your assistance!
All drives start at the same time.
We are selling him the Drives. He is asked for help sizing the wire and Circuit protection devices.
I used 430 part X to size the wire per servo input current.
The Servo is listed as having overload protection for the Servo motor.
I sized the circuit breaker based on Servo input current and table 430.52(C)(1) for a synchronous motor at 250% of the current.
The client is telling me they have never sized the CB's for similar Servo's as large as we recommended.
looking at the system it looks like someone specified a servo system larger than needed, When looking at a total of 13 drives the current really adds up.
They have typically sized the main control breaker for the machine at 30 amps. If I add up all of the rated input currents to size the main control panel breaker I am at closer to 200 amps.
So here are a few questions.
1, was I wrong using 430.52(C)(1) at 250%?
2. Is it acceptable to size the wire as stated above, but size the CB's based on empirical data?
3. The method I used to size the Main Control Breaker was sizing the main panel breaker still a sum of all loads (current) except the largest load, added to the largest breaker. Is this still acceptable or should I look at another method?
Thanks in advance for your assistance!