Here at work the question was brought up of what gauge primary wire should be provided for our LED drivers. The drivers are multi tap:
120v - 277v input / 12vdc output
1.05a @ 120v /.85a @ 208v/ .55a @ 240v / .51a @ 277v
Operating range of 90vac - 285vac
Max load of 1.5a @ 90vdc per driver
The question is, when communicating to the customer what size wire to have their electrician bring to the source, should we tell them the max possible load it could draw @ 90v or the actual load based on the voltage they will be using (usually 277v)? One may require #14 where the other may require #10. What if someone rewires the drivers for 120v at a later date? Now that #14 is too small. Common sense would tell you to use the wire size required for max possible load. In this case 1.5a per driver @ 90v. Would love to know where to find the correct answer in the NEC as well.
Thanks,
120v - 277v input / 12vdc output
1.05a @ 120v /.85a @ 208v/ .55a @ 240v / .51a @ 277v
Operating range of 90vac - 285vac
Max load of 1.5a @ 90vdc per driver
The question is, when communicating to the customer what size wire to have their electrician bring to the source, should we tell them the max possible load it could draw @ 90v or the actual load based on the voltage they will be using (usually 277v)? One may require #14 where the other may require #10. What if someone rewires the drivers for 120v at a later date? Now that #14 is too small. Common sense would tell you to use the wire size required for max possible load. In this case 1.5a per driver @ 90v. Would love to know where to find the correct answer in the NEC as well.