I work for a company that manufactures industrial equipment with listed industrial control panels. Many of these have 1-3 VFDs and a mix of other loads, including a 24VDC power supply and smaller, fixed speed fans. We have gotten many questions from customers regarding our published supply wire sizing recommendations for variable speed control panels. We use the requirements of 409.20 to calculate required ampacity, taking the VFD input current rating as the full-load current rating of motor loads rather than the actual motor load per the requirements of 430.122. We use the following formula to calculate the required ampacity for a machine:
(1.25 * largest VFD input current rating) + remaining VFD input current rating + FLC off all fan motor loads + (1.25 * 24VDC control power supply input FLC rating)
We believe this method to be correct with NEC, but are there any comments or corrections that we should consider in our calculations?
(1.25 * largest VFD input current rating) + remaining VFD input current rating + FLC off all fan motor loads + (1.25 * 24VDC control power supply input FLC rating)
We believe this method to be correct with NEC, but are there any comments or corrections that we should consider in our calculations?