I need advice so that a debate can be settled.
A new machine is being installed in the plant I work at. Part of the machine is fed by a 460 vac, 3 phase 800 amp panel and the main OCPD for the panel is set at 800 amps. I looked at the size of the wires that the EC pulled in and found that they pulled in 2 sets of THHN 400 kcmil's, copper. It is my understanding, that without taking any derating factors into account, that the paralleled ccc's would only be good for a maximum of 760 amps, going off of table 310.16. I questioned the person that is overseeing the installation and his response was "the EC said that according to his charts and calculations, they have the right wire size".
But, on another area of the machine, they pulled in 2 sets THHN 500 kcmil's, copper, for a 600 amp panel.
I keep asking to see what charts, tables or calcuations they used to come up with the wire sizes, but I keep getting the run-around.
I also think the conductors should be de-rated for temperature because the conduit that they are in run close to the ceiling for at least 50'(ceiling height of approx 30') and in the summer time, the temperature can easily exceed 110 degrees F. Even in the winter it is around 90 degrees.
Is my train of thought on the right track or am I misguided in my efforts?
A new machine is being installed in the plant I work at. Part of the machine is fed by a 460 vac, 3 phase 800 amp panel and the main OCPD for the panel is set at 800 amps. I looked at the size of the wires that the EC pulled in and found that they pulled in 2 sets of THHN 400 kcmil's, copper. It is my understanding, that without taking any derating factors into account, that the paralleled ccc's would only be good for a maximum of 760 amps, going off of table 310.16. I questioned the person that is overseeing the installation and his response was "the EC said that according to his charts and calculations, they have the right wire size".
But, on another area of the machine, they pulled in 2 sets THHN 500 kcmil's, copper, for a 600 amp panel.
I keep asking to see what charts, tables or calcuations they used to come up with the wire sizes, but I keep getting the run-around.
I also think the conductors should be de-rated for temperature because the conduit that they are in run close to the ceiling for at least 50'(ceiling height of approx 30') and in the summer time, the temperature can easily exceed 110 degrees F. Even in the winter it is around 90 degrees.
Is my train of thought on the right track or am I misguided in my efforts?