Wire size contradiction

Status
Not open for further replies.
You reading the 90 degree C column. There are really no terminations rated for 90 degrees C so you must use the 75 degree column which means #4/0 Cu for 225 amps.
 
I see. Just out of curiousity, why does table 310.16 show all the different types of wire and temperature ratings when equipment terminals are universally rated for 75 degrees, therefore reducing the allowable ampacities to such?
 
Rawls007 said:
I see. Just out of curiousity, why does table 310.16 show all the different types of wire and temperature ratings when equipment terminals are universally rated for 75 degrees, therefore reducing the allowable ampacities to such?

You may use the 90C to derate as long as the final OCPD is not larger than the 75C column will allow. This is helpful when pulling more than 3 current carrying conductors in a conduit. See T.310.15(B)(2)(a)
 