What size of AWG is required for a 200A main breaker to the meter base?

The run from the main breaker to the meter base is about 2 ft. Was at the local electrical shop today and got some material and was inquiring on the price of conductors for the 200A main breaker to the Meter as I am not sure if I need it or not, til the meter gets pulled.

After telling the guy I only needed 7 feet because the meter is directly behind the panel, He went to his scrap pile and gave me 7 feet of 2/0 xlpe 600v copper wire for free and said that this is good for what I needed it for. I wanted to confirm that this is ok to use. Don't want to take his word as I want to make sure. Although I did google it and found 190 A on one chart. Got to get my code book back from Bro who wanted to look up the requirements for a cabin.

Will post pics of final install for ya all to slap me silly on any thing you may deem WTF ?? Just hate having to install several junction boxes close to the panel so I can extend the wires and have plenty to work with.


~FyE~
 

Buck Parrish

Senior Member
Location
NC & IN
2/0 cu. is good for a sfd only.
It's not quite rated for 200 amps. But your allowed to go to the next breaker size which is 200.
So your all right. And it's free!!


Lots of guys use 4/0 al
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Under the US NEC, using normal connectors rated at 75C, the 2/0 conductors have an ampacity of 175A.

Under the US NEC, however, such conductors are considered suitable for a 200A residential service.

If the Canadian Electrical Code has the equivalent of the US NEC table 310.15(B)(6), then you should be good to go.

-Jon
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
winnie said:
Under the US NEC, using normal connectors rated at 75C, the 2/0 conductors have an ampacity of 175A.

Under the US NEC, however, such conductors are considered suitable for a 200A residential service.

If the Canadian Electrical Code has the equivalent of the US NEC table 310.15(B)(6), then you should be good to go.

-Jon

Yeah but aren't Canadian amps bigger than American amps?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe xlpe is an underground utility cable and is not recognized by the NEC. I don't know about the canadian code.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
1stYearElectrican said:
Thx for the reassurance folks, Man I miss my code book.

~FyE~

Who puts out the Canadian Electrical code?
The NFPA does the NEC, and there is a free version on their website. Maybe there is something similar for the CEC.
 