This is for a small office. The engineer says it has to be a 250 amp service using 3-0 copper wire
The load calculations I did I came up with 150 amp load. Building is less than 2800 sq/ feet and it just offices for 5 people.
Inspector failed my 200 amp 240V single phase service with 3-0 wire, because the engineer said it needs 250 even though I showed him my load calculations.
So I installed a 6’ tall 400 amp capacity semens panel board with a down sized 250 amp main breaker.
He passed the service and panel all good this time. I used 4-0 copper and 2 10’ ground rods with #2 wire.
This panel is 35’ from the inside sub panel
I was going to run 4/0 copper for the hot 3/0 for the neutral and #2 for the ground. Wanted to get another opinion on this. There are no unbalanced loads
Inspection is not going to know any better because he said 3/0 was a good wire size.
Thank you for any help.