I am installing a peice of equipment on and existing curcuit that has a 25a breaker and 12g wire. Is 12g sufficient for a 25a curcuit, it is 3 phase commercial.
rjhavens1 said:I am installing a peice of equipment on and existing curcuit that has a 25a breaker and 12g wire. Is 12g sufficient for a 25a curcuit, it is 3 phase commercial.
rjhavens1 said:It is a Refrigeration condensing unit with a fused disconnect with 25a fuses
rjhavens1 said:the maximum over currenent protection is 30a the minimum is 16.4a
don_resqcapt19 said:Actually in that case the code would permit the use of #14 with the 30 amp OCPD.
Don
Here is the problem or solution---article 310.16 has an asterik that relates to article 240.4(D). This article, in the the first sentence, says Unless specifically permitted in article 240.4(E) or (G) the overcurrent protection shall not exceed 15 amps for 14, etc. However, 240.4(G) states the permission to disregard (D). Remember (D) states unless otherwise permitted--(G) is where it is specifiically permitted. In your case it is refrigeration. Since 14 gauge is good for 20 amps (Table 310.16) 75 DEGREE, you can then use 14 gauge wire for the 16.4 amp load. Now I would run 12 guage and according to article 440.22 (A) 2nd sentence you can use an OCP rated at 175% of the motor compressor load--- 16.4 times 175%= 28.7 AMP ocp-- THEREFORE 25 AMP IS FINE WITH #12-- yOU HAVE TO USE 75 DEGREE RATINGS BECAUSE THE BREAKERS ARE ONLY RATED AT 75 DEGREErjhavens1 said::smile: Thanks for all the help guys, but my boss wants proof in the code book on where it says it is ok to run 12awg on a 25a OCPD for the load that I have described. On Table 310-16 , 12thhn has a 90degree rating. The table shows 30amp capacity with a obelisk next to the rating. According to the bottom of the table it states the OCPD with conductors marked with obelisk shall not excedd 15a for 14awg and 20a for 12awg. Is there something we are missing?:-?
It's a little bit tricky to convey - because there's not a clear sentence that flat out says the practice is okay. We're kind of trying to describe a vacuum, in a way. I agree with Dennis' read on this, but I want to put it a little differently.rjhavens1 said::smile: Thanks for all the help guys, but my boss wants proof in the code book on where it says it is ok to run 12awg on a 25a OCPD for the load that I have described.
Right, 310.16 is the first step. Terminations are generally rated at 75 degrees, but anything under 100A could have 60 degree terminations, too. See 110.14(C)(1) for more information, too.On Table 310-16 , 12thhn has a 90degree rating.
It does?The table shows 30amp capacity with a obelisk next to the rating.
Yes, you are. Think of it this way: Why would they bother giving us ampacities if they always had to be breakered #12 to 20A, #14 to 15A, etc?According to the bottom of the table it states the OCPD with conductors marked with an asterisk shall not exceed 15a for 14awg and 20a for 12awg. Is there something we are missing?:-?