Hey guys, I have a 1200 amp 3ph 480v main breaker panel to install. For the wire sizing do I need to have conductors large enough to carry 1200 amps on each leg or conductors to carry 400 amps per leg ?
Thanks
EGC's...sure that right.
N's are return path.
EGC's...sure that right.
N's are return path.
???
Wanna elaborate? I am not quite sure what you are trying to say.
1200 amp Service means no EGC's.
1200 amps per leg, as has already been mentioned. Also keep in mind requirements in 240.4(B) for over 800 amps - you can not use next size higher overcurrent protection so commonly seen use of 500 copper which has ampacity of 380 can be protected at 400, the next size device. But for over 800 amps you can't run three parallel sets of 500 as they only have a combined ampacity of 1140 amps.Hey guys, I have a 1200 amp 3ph 480v main breaker panel to install. For the wire sizing do I need to have conductors large enough to carry 1200 amps on each leg or conductors to carry 400 amps per leg ?
Thanks
Is copper busbar an option in this case?Each set of phase conductors will have to total at least 1,200 amps the NEC allows a smaller neutral in some cases.
For us a 1,200 amp feeder is often three sets of 600 kcmil copper.
So that is a total of 12 - 600 kcmil (3A, 3B, 3C, 3N) and 3 appropriate sized EGCs for a 1,200 amp breaker.
Is copper busbar an option in this case?
I'm thinking you would probably need spreader bars in any case to land all the cables.
OP was landing on a 1200 amp main breaker in the panel, it likely had 3 or 4 port lugs that accept up to maybe 750kcmil conductors per port. But had it been a main lug only panel it still likely has similar 3 or 4 port lugs for main lugs.Is copper busbar an option in this case?
I'm thinking you would probably need spreader bars in any case to land all the cables.
Likely it is but by a long margin a 1,200 amp circuit in my area will be done with muiltiple wire conductors of aluminum or copper. I even see circuits up to 4,000 amps run using wire.
Around here busway seems to start being looked at above 2,000 amps and often used when the electrical rooms are stacked so a vertical busway can be installed with multiple plug in tap provisions at each floor.
I really can't say why we don't use more of it. Maybe as simple as the way the pricing works out.
Busway uses less space but may cost more to purchase and install?