If you are talking about what size the AC supply conductors should be, simply look at the manufactures recommend breaker and wire sizes. All I have ever designed is based on the OCPD. The AC supply is not that important since you are working with a self regulating SDS device.
The DC supply conductors is a completely different story. They are based on voltage drop from the battery terminals to the load. The industry loop voltage drop levels are:
48 VDC Plant = 2 VDC
24 VDC Plant = 1 VDC
12 VDC plant = 1/2 VDC
You have to divide the sections of the system up to end up with the maximum VD. Example on a 24 VDC plant is usually divided into three sections. Battery Terminal-to-Charge Bus, Main Power Board-to-Breaker Bay, Breaker Bay-to-Load device. Typical voltage drop for each section may look like this:
Battery Terminal-to-Charge Bus = 1/8 VDC
Main Power Board-to-Breaker Bay = 1/4 VDC
Breaker Bay-to-Load Device = 5/8 VDC
Voltage drop is calculated by:
(22.2 * L * I) / VD = CM
Where
22.2 = Constant for copper @ DC
L = Length in feet one-way distance
I = Maximum Load Current In Amps
CM = Circular Mills Of Copper Cable Needed
Once you figure the conductor sizes, cross-check with table 310-16 to make sure the conductors are at least the minimum recommended. This is not usually a problem unless very short distances are encountered.
The other important thing is connector resistance all connectors should be irreversible compression connectors two-hole tongue type, and "NO-OX" should be used on the wire skinner and between contact surfaces.
Hope that helps.