wire size for a pool pump

Status
Not open for further replies.

slumps37

New member
I got a pool pump that on a 110 circuit it pulls 18.5 amps and on a 230 circuit it pulls 9.6. Right now it is temporarily set up for 110 but it recommends 230. My question is that the disconnect that I got is a 50 amp disconnect and if I have to run wire capable of 50 amps even though the pump will never pull the full 50 amps so I was wondering what size wire gauge should I use. Or is there an alternative to my problem
 
Re: wire size for a pool pump

hey slumps, 50A is the maximum on that A/C disconnect, there is no minimum. written on the disconnect is the legal wire size range for it's lugs. like "line in lugs #6 - #14".

680.21 (A) (4), 2002 code, will let you run 12/2 with groud romex, to the disconnect. IF: 1. one family dwelling 2. romex only runs inside the house 3. no other piece of pool equipment is on that circuit.

otherwise, the circuit must be piped(680.21 (A) (1)), with a minimum #12 insulated green grounding conductor.

if you use a breaker as your disconnect, the panelboard must be fed with a min of 30A (215.2 (A) (2)). therefore, #10s and the grounding conducter must be insulated and green. the run must be piped (680.25 (A))
 
Re: wire size for a pool pump

Originally posted by poolsparky:
otherwise, the circuit must be piped(680.21 (A) (1)), with a minimum #12 insulated green grounding conductor.
MC Cable is quicker and easer. :)
 
Re: wire size for a pool pump

Originally posted by electricman2:
pull # 10 wire
Why #10?
cause i LIKE upsizing wire on motors and such
just because all i HAVE to run is #12 doesnt mean thats what i will run, especially on my own stuff...

A/C unit pulls 19 amps at 240? #6 wire baby!!!
 
Re: wire size for a pool pump

izak,
cause i LIKE upsizing wire on motors and such
but why, and why would you tell Slump37 to use a larger than necessary conductor without putting this disclaimer in your first post?

just because all i HAVE to run is #12 doesn't mean thats what i will run,
In the original question a # 14 (with a # 12 EGC) would be all that you would HAVE to run.

Roger

[ October 16, 2004, 01:03 AM: Message edited by: roger ]
 
Re: wire size for a pool pump

why do i like upsizing wire on motors?
they tend to run more efficiently that way

why did I 'not add my disclaimer' ??
because it was an Opinion
which is alot of what i see on this board

larger wire is Never wrong In My Opinion,
if you can afford it
plus it leaves room for future...
like.. putting in a larger motor

sorry, but Ive watched alot of Tom Henry's videos, and he is big on upsizing wire when its practical
 
Re: wire size for a pool pump

Branch circuits for pools can be installed using the proper 'type' MC cable, but is most likely not the standard method.
Feeders for pools cannot use MC cable, there are only 4 wiring methods permitted for feeders, with 2 additional types that have restrictions to the installation parameters.

Pools/Spas seem to cause some consternation for electricians that I come across. I believe one of the reasons for that is 'supplyhouse talk'. Too much misinformation being thrown around.
If you were to take a look at any bookstore or online source for books, you will see very, very few books that deal with pool wiring. Even the pool suppliers have very little info available... Hmm... do we have any potential authors out there?
 
Re: wire size for a pool pump

Originally posted by Pierre:
Branch circuits for pools can be installed using the proper 'type' MC cable, but is most likely not the standard method.
I am not sure what you mean about the proper type.

680.21(A)(1) requires MC listed for the location, not the application. :)

In other words use MC in dry locations unless you get the MC type listed for wet locations.

Using MC is a common method in this area, MC from panel to sill then change to PVC for outside. :)

Of course if you got the right type of MC you could run it all the way to the pump.

We call it parking deck MC but it is MC with a liquidtight jacket. ;)

Looking at 330.10(A)(12)(c) any of the MC I commonly use could go all the way to the pump.

[ October 16, 2004, 05:47 PM: Message edited by: iwire ]
 
Re: wire size for a pool pump

I usually run mc from the panel to the sill and then switch to conduit to go outside to the pump. If the basement is open and easy I will just run PVC right to the panel. Why make things harder than they ought to be?
 