I'm in the middle of a kitchen remodel and decided that the easiest way to run the additional circuits I now need (house was built in the 80s) was to run a new subpanel from the main panel in the basement up to the garage which is next to the kitchen.
I asked the electrical inspector what size wire I needed for a 125 amp subpanel, and he told me to use SER cable, #3 aluminum or #4 copper. Looking at the NEC ampacity chart though, it looks like that's not even enough for 100 amp service, much less 125 amp. The electrical inspector did sound like he was quoting off the top of his head versus actually looking something up. Am I missing something in the NEC code, or did I get bad advice? What size cable would you use for this?
The run is about 25' long, it's going up an exterior wall, through the attic, and then run down through EMT conduit to the surface-mount panel. The conduit is just for physical protection.
I asked the electrical inspector what size wire I needed for a 125 amp subpanel, and he told me to use SER cable, #3 aluminum or #4 copper. Looking at the NEC ampacity chart though, it looks like that's not even enough for 100 amp service, much less 125 amp. The electrical inspector did sound like he was quoting off the top of his head versus actually looking something up. Am I missing something in the NEC code, or did I get bad advice? What size cable would you use for this?