this is a 3 part question, each related to this topic.
i have heard about a job where the contractor used #18 tffn wire from his control panel to the field devices in rigid conduit. the distance was anywhere from 25 ft to 200 ft away. his control voltage was 24 volts dc and 110 volts ac.
these devices are photo cells, encoders, and solenoid valves.
these devices are controlled by a programmable controller. the maximum output current from the plc is 4 amps (4 outputs per common fuse).
article 725 allows #18 for power limited circuits of 30 volts or less and 1000 va max.
Question #1.
isn't a 110 volt ac circuit on a # 18 awg stranded wire in violation of article 725 or have i missed something.
Question 2.
what should the wire size be for these devices?
my answer is #14 based upon Nec 2002 article 310.5.
Question 3.
what is the wiring classification of the plc inputs/outputs? class 1,2,3, power limited?
thank you in advance.
i have heard about a job where the contractor used #18 tffn wire from his control panel to the field devices in rigid conduit. the distance was anywhere from 25 ft to 200 ft away. his control voltage was 24 volts dc and 110 volts ac.
these devices are photo cells, encoders, and solenoid valves.
these devices are controlled by a programmable controller. the maximum output current from the plc is 4 amps (4 outputs per common fuse).
article 725 allows #18 for power limited circuits of 30 volts or less and 1000 va max.
Question #1.
isn't a 110 volt ac circuit on a # 18 awg stranded wire in violation of article 725 or have i missed something.
Question 2.
what should the wire size be for these devices?
my answer is #14 based upon Nec 2002 article 310.5.
Question 3.
what is the wiring classification of the plc inputs/outputs? class 1,2,3, power limited?
thank you in advance.