I have a new pad mounted 75 kva transformer (13.8 KV - 480Y/277V 3PH, 4W). The transformer needs to be grounded but I was unsure about the size of the grounding conductor. The conductors for the secondary side of the transformer are sized as 1/0 copper. Looking at Table 250.66 it seems that I can size the ground conductor as small as #6 copper. According to Table 310.16 the ampacity of #6 is 65 amps but on the seconary size, the transformer will draw (75000kva)/(480V)(1.73) = 90.32 amps at full load. Is this the proper way to size the ground or should I go one cable size larger? I would appreciate any help as always. Thank you, patrick