wire size for x0 xfmr. bond?

Status
Not open for further replies.
ERIK@DDE said:
Do i apply nec 250.66 @ the primary, or the secondary side wire size for my neutral conductor bond ?
It would be based on the secondary conductors.

(1) System Bonding Jumper An unspliced system bonding jumper in compliance with 250.28(A) through (D) that is sized based on the derived phase conductors shall be used to connect the equipment grounding conductors of the separately derived system to the grounded conductor.
.
 
I would add that table 250.66 only goes up to 1100 kcmil. If your secondary conductors are larger than 1100 kcmil you'll need a system bonding jumper sized at 12.5% of the secondary conductor's size.
 
Yes I Agree.. But

Yes I Agree.. But

I have 2sets of 250kcm pri. and one set 500kcm sec. ? what do i base my conductor size ( x0 bond ),on. pri. or sec. ?
FYI- 480 v -480/277 ,225 kva ,G.P. xfmr, delta-wye.cnfg.
 