That is absolutely true for OP.It will have to be answered by someone familiar with CEC.
My builders electrician was running what I thought to be an undersized wire to panel...
It hasn’t been installed yet...
He didn't give enough details to confirm anything though. That would cover what is likely majority of time with what little info we have.I believe the CEC is similar to NEC in wire size. IMO, it would be 4/0 aluminum at the minimum. It may also require 250 kcm.
What size is the electrician running? Isn't the job getting inspected?
my version is pretty old now but I don't think its changed.CEC said:For 3-wire 120/240 V and 120/208 V service conductors for single dwellings, or for feeder conductors supplying
single dwelling units of row housing of apartment and similar buildings, and sized in accordance with
Rules 8-200(1), 8-200(2), and 8-202(1), the allowable ampacity for sizes No. 6 and No. 2/0 AWG shall be 60 A
and 200 A, respectively. In this case, the 5% adjustment of Rule 8-106(1) cannot be applied.