For years now I have used the 90 degree column to size my conductors. I have always used 2/0 for 200 amp underground feeders
I am being told I have to use 3/0 copper for 200 amps on a small design build we are bidding
The reason I was given is that since the lugs on the panel are only rated 75 degrees c I must use that column to size my conductors.
Has anyone else heard of that???
Even if I do use the 75 degree column the conductors leave a bottom fed panel, go directly underground to the transformer, buried 3 1/2 feet deep. That would make the ambient temp 70 or so degrees. So 2/0 is good for 175 amps in the 75 degree column. Correction factor is 1.05
175 X 1.05 = 183.75 amps. 240.4. B allows me to go up to the next standard size... 200 amp
Am I missing something??
I am being told I have to use 3/0 copper for 200 amps on a small design build we are bidding
The reason I was given is that since the lugs on the panel are only rated 75 degrees c I must use that column to size my conductors.
Has anyone else heard of that???
Even if I do use the 75 degree column the conductors leave a bottom fed panel, go directly underground to the transformer, buried 3 1/2 feet deep. That would make the ambient temp 70 or so degrees. So 2/0 is good for 175 amps in the 75 degree column. Correction factor is 1.05
175 X 1.05 = 183.75 amps. 240.4. B allows me to go up to the next standard size... 200 amp
Am I missing something??