If I set a 200A, 8-space, meter/main and then install a 100A breaker to feed the dwellings main panel, I get to use Table 310.12 to size the wire for the main panel so I would use #2 AL, according to 310.12 (A) and (B), which points me to Table 310.12. All good so far right?
Ok, If I also install another 100A breaker to feed another panel in the basement I would not be able to use table 310.12? Is that correct? In this case I would set a 90A breaker and use #2 AL from past experience, but I don't know why this allowance is only for the main panel or as code words it, conductors supplying entire load.
My question is: I don't know why I can't use table 310.12 for both feeders?
Would I be able to use table 310.12 at all if I installed both panels at the same time, and got it inspected all at once?
This is not something I am going to do. Just trying to understand the rule.

Ok, If I also install another 100A breaker to feed another panel in the basement I would not be able to use table 310.12? Is that correct? In this case I would set a 90A breaker and use #2 AL from past experience, but I don't know why this allowance is only for the main panel or as code words it, conductors supplying entire load.