I removed a old roof top unit 208v 3p on a 400a breaker. I will be using that existing breaker and the 3in EMT feeding up to the roof. It will now be feeding two RTU's with MCA's of 122a each and MOCP of 150a. I will split the wire at the two fused disconnects next to each other. Can i size the wire for 244a or must it be sized for 400a? john