Wire size

Status
Not open for further replies.

70ramair

New member
I would like to determine correct wire size for a 100 amp 240 volt single phase sub panel 300 ft from the main panel. Any one have a calculator for the voltage drop/ wire size? If I ran (3) #2 THHN's and (1) #6 in 2" SCH 80 PVC 300' what would the conductors ampacity be derated to?
 
Re: Wire size

If your calculated load is 61 amps or less than you would have a voltage drop of 3% or less. As Peter mentioned you'll need to know the calculated load since this is one component of the voltage drop formula. Take a look at this voltage drop calculator:

http://www.electrician.com/vd_calculator.html
 
Re: Wire size

Originally posted by 70ramair: . . . what would the conductors ampacity be derated to?
They would not be "derated." The ampacity is first determined from the size of the conductor, its material of construction (copper versus aluminum), and its insulation type. That ampacity would be derated if you installed more than three current-carrying conductors in the same raceway, or if the ambient temperature exceeded 30C.

If you choose to use a larger wire than is needed to support the current drawn by the load, and if that choice is based on voltage drop considerations, you are not changing the ampacity of any conductor. Rather, you are choosing a conductor with lower resistance. As a side benefit, but an unrelated benefit, you get a conductor with a higher ampacity.
 