And if this journeyman knew how to apply the applicable articles and was correct in using a #14 landed on a 20 amp (or even a 30 amp) breaker, what basis would you use to fire him.Originally posted by GENEM:
If one of my journeyman landed a #14 on a 20a breaker in a branch panel, he would be looking for a job. Especially if he did not know what he did wrong. :roll:
It this application he would have done nothing wrong. If he were wiring according to the AC mentioned in the original post than why should he be fired for following the code? As others have mentioned it seems like it's his boss that needs some code review.If one of my journeyman landed a #14 on a 20a breaker in a branch panel, he would be looking for a job. Especially if he did not know what he did wrong
I suspect this thought process is why I see so many AC units wired with conductors sized to the maximum breaker size. :roll:Originally posted by GENEM:
If one of my journeyman landed a #14 on a 20a breaker in a branch panel, he would be looking for a job. Especially if he did not know what he did wrong. :roll:
I don't think going along with someone's ignorance is the best idea. If a so-called inspector is ignorant of the most basic things like sizing conductors for a motor, I wouldn't listen to a word he said. Furthemore, if this inspector is ignorant, he may not be very safe at all!Originally posted by GENEM:
So if it comes down to which is right--I will go with the ignorance of the inspector and play it safe.
The issue I see is,Originally posted by GENEM:
By the way-we are speaking of motors here- if it is an a/c check 440.6 for conductor size.
This is an unfair statement. If you canned someone for doing this, you're wrong. If he "did not know what he did wrong" then obviously the "don't contest inspectors under any circumstances" rule in your company was not very plain.If one of my journeyman landed a #14 on a 20a breaker in a branch panel, he would be looking for a job. Especially if he did not know what he did wrong.
240.4(D), referencing (G) specifically explicitly excludes A/C's from the rule.240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed...