sparky
Member
- Location
- Pennsylvania
Recently installed a 3/0 208 volt line to serve a compressor that i thought would be 15hp. Customer installed a 20 hp air compressor after job was complete. I get a call that his motor has burned out because my wire was to small. Upon investigating i find the 20 hp motor. But I have #6 copper feeding this.According to my calculations 20 hp motor is rated at 59 amps . 59 amps x125%= 74.5 amps #6 wire is rated at 75 amps this wire still should have been large enough. air compressor is in a unheated shed where temp are well below freezing i think the cold made the motor start hard any thoughts?